KE100/KH100 invalid Matter implementation - heating status, Home Assistant
KE100/KH100 invalid Matter implementation - heating status, Home Assistant
I just enabled Matter in Kasa app and added KH100 hub with KE100 thermostat valves to Home Assistant. I used these already in HA, but through unofficial integration plugin.
Problem: thermostat valves report "heating" whenever they are "on" (i.e. not in anti-freeze mode) regardless of the temperature and open/closed radiator. For example, there's 20°C detected in the room and 18° set, so the valve remains closed until the actual temperature drops below the latter value and there's a need for heating again. But even in this state, Home Assistant shows the device as "heating". While this behavior is consistent with green/grey on/off status shown in Kasa app, it is illogical and definitely needs to be changed both in the app and in Matter. In reality, "heating" is actually happening only when the radiator valve is open. There's no difference between "off" in app (with anti-freeze) and "off" when set temperature is lower than measured - in both cases the valve is closed and "off". I don't know why your implementation doesn't follow this reasoning.
I rely on "heating" (demand!) status to automate gas boiler operation, so swapping the existing HVAC entities with the ones from Matter broke the whole thing. It's really important.
Also it would be great if you could add hysteresis setting or fully manual open/close operation e.g. for floor heating. With external thermometer it is usable, but not exactly what I need.
- Copy Link
- Subscribe
- Bookmark
- Report Inappropriate Content
The valve will not close completely even when the temperature reaches the set temperature. If the valve is completely closed, the temperature is going to drop rapidly.
KE100 will adjust the opening and closing ratio according to the temperature change in order to maintain the temperature in a stable range.
- Copy Link
- Report Inappropriate Content
This is not what I observe, otherwise I would just return or sell all thermostats. The sound of valve closing is exactly when my current system reports "not heating" = off. And the other way around. Also I can accurately hear when the water is flowing and when it's not (or just sipping, which seems to be fine). For example, today the boiler is running for 7 hours and the radiator which should be off is a little cold to the touch (valve in "mode 2” below) exactly like the one next to it which is closed by analog means. Knowing the exact opening percentage would be nice, though.
You (TP-Link) need to understand that not everyone has constant supply e.g. from municipal heating plant. We have gas boilers, heat pumps etc. which work only when necessary. To automate our homes we need information from each thermostat if it's currently open (heat demand) or closed (even if not completely).
Basically right now there are three modes:
1. OFF in the app, effectively anti-freeze
2. ON in the app, when the measured room temperature is higher than needed and the valve is (mostly) closed. It's on standby, ready to be opened when needed. Valve must not report it's ON and "heating" when in fact it's not!
3. ON in the app and actually heating the room.
The only difference between 1 and 2 is the temperature! If you set the same value in 2 as anti-freeze, what's the difference? Only in reporting.
Also could you please confirm that my issue has been forwarded to the relevant teams and recorded as a potential bug? Again - it is illogical. Matter is in Beta so it is really important to give them feedback.
- Copy Link
- Report Inappropriate Content
Home Assistant entities are exactly the same, just the reported state differs. Via unofficial integration it's "off" now, while via Matter it's "heat". So definitely Matter implementation in Kasa hub is causing this:
hvac_modes: off, heat
min_temp: 5
max_temp: 30
current_temperature: 20.8
temperature: 20
friendly_name: XXXXX
supported_features: 385
Similarly via "official" HA integration for TP-Link I just installed, it's "heat". But this time there's also:
hvac_action: idle
... which can be used in my automation instead of off/heat. And further confirms that Matter is broken as of now.
@Wayne-TP Also could you please confirm that my issue has been forwarded to the relevant teams and recorded as a potential bug? Again - it is illogical. Matter is in Beta so it is really important to give them feedback.
- Copy Link
- Report Inappropriate Content
How do you use KE100 for temperature control? Through Kasa's Smart Control (schedule) function? Manually adjust the temperature in the Kasa app and manually turn off the KE100 when the set value is reached? Or a simple turn on/off control through Home Assistant?
- Copy Link
- Report Inappropriate Content
- Copy Link
- Report Inappropriate Content
Could you please confirm that potential bug has been reported to the devs? Or are you going to ignore it altogether on behalf of your employer?
- Copy Link
- Report Inappropriate Content
Through research and discussion with relevant personnel, I learned that the Matter standard currently defines only two operating modes for thermostat devices: heating and off. Hence KE100's Matter compatibility also follows these standards.
If Matter gives more details for this type of device and includes additional functionalities in the future update, our devices will also start adaptation gradually.
- Copy Link
- Report Inappropriate Content
I found the following on Home Assistant forum:
"The HA Matter integration supports hvac_action if the device provides the “ThermostatRunningState” attribute, so this isn’t a limitation in HA:"
https://community.home-assistant.io/t/nest-thermostat-hvac-action-in-matter-integration/601480/7
I briefly searched the ”Matter Application Cluster Specification 1.3” and found this:
"4.3.9.34. ThermostatRunningState Attribute
This attribute SHALL indicate the current relay state of the heat, cool, and fan relays.
Unimplemented outputs SHALL be treated as if they were Off."
This is different from ThermostatRunningMode which seems to be on the higher level:
"4.3.9.27. ThermostatRunningMode Attribute
This attribute SHALL indicate the running mode of the thermostat. This attribute uses the same val-
ues as SystemModeEnum but can only be Off, Cool or Heat. This attribute is intended to provide
additional information when the thermostat’s system mode is in auto mode."
And, the most important, OFF in RunningMode is defined as "The Thermostat does not generate demand for Cooling or Heating" - DEMAND seems to be the key for the logic and is in line with how I think it should work.
By the way, Tapo and Kasa apps interpret it differently: with no heat demand in idle, Tapo shows "heating off" (while main switch is still "on" in blue), but Kasa says "heating to X" even with X lower than measured in the room (main switch "on" in green). I switched to Tapo as its UI is so much better!
Could you please consult the devs again?
- Copy Link
- Report Inappropriate Content
I find lack of this information to be quite annoying. My old system did report percentage of the vale "open state" so if it was 0% it's closed (and not heating the room) and 100% was fully open. It was good as it allowed to monitor what the system is doing and identify issues like air in the heater (if it reports open but it's cold then you know something is wrong.)
Kasa only reports "heating" as a "ready" state ("not off") And only place that shows if the valve was opened is on the historical chart.
in that case heating/off/antifreeze is more like a mode. But there is no information about a state (opened and how much/closed)
My request would be to be able to see:
- is that particular valve open (heating) or not - might simply change the icon color on the list
- on the detail page for that valve - how much is it opened? 5% 100%?
- ability to set offset for that valve - not the temperature offset but how much it should be opened (compensated). I use external T315 for most rooms. So if there are some issues in how the valve works, or how the heater is connected, it can be compensated so that they heat uniformly.
- Copy Link
- Report Inappropriate Content
Kasa app does not show heating status (except in history chart), but Tapo does.
And of course Home Assistant, but through TP-Link plugin (unofficial) instead of Matter. There is also unofficial Tapo plugin in HACS but it's broken right now and seems a bit abandoned, only older version still works.
There is no option to display valve %, probably because the hub does not share this info with the cloud service or locally. It would be nice to have it, but it's not a deal breaker for me.
- Copy Link
- Report Inappropriate Content
Information
Helpful: 0
Views: 1227
Replies: 14
Voters 0
No one has voted for it yet.