@BrianDipert Do you have a picture of the wireing of the old switch?
1HELPFULS
Forums/
Kasa Smart Switches
2020-05-06 20:15:47
@S2005 If you just change the one switch in box1 you would not need to run the romex
1HELPFULS
Forums/
Kasa Smart Switches
2020-05-06 19:22:34
@S2005 Mark the existing white that goes from box1 to box2 with black tape(so you know it is a traveler) Run a white neutral from the other whites in box1 to box2 to be used for box2 HS210...
3HELPFULS
Forums/
Kasa Smart Bulbs
2020-05-06 19:11:04
@Steve_______ Because it is low voltage, it should be OK as long as you do not put it in the same box with house wiring.
1HELPFULS
Forums/
Kasa Smart Switches
2020-05-06 19:05:38
@S2005 In Box 2 connect black to common/load, red and white are travelers. You will need to run a neutral from box1 to box2. In box 1 connect black from Hot In to common/load, red and white are...
4HELPFULS
Forums/
Kasa Smart Switches
2020-05-02 11:49:08
@Azazel Without a neutral you are out of luck
1HELPFULS